beechigby
Member
- Location
- St. Croix US Virgin Islands
I have 16 215w microinverters, (.9A ea)=14.4A, 240Vac; #12 THWN-2 wire in 3/4 conduit, (2 CCC, 1N, 1EGC, and #6GEC, 5wire total) and a 240Vac 30 Disco (Term.rateing 75degC)
I have an ambient temp of 26-30C and an addr for rooftop of 33degC= 63deg C to enter T310.15 B 2 a
#12 has ampacity of 30A x .65=19.5Amps. this means I can have up to 19.5 calculated Amps running thru this wire, correct?
OR; becuause the #12 is termianted at the 75 deg switch, I must use the 75deg col. of T310.15 B 2 a, which has a factor of .47 x 30A = 14.1Amps of Ampacity, which is .3 amps less than my calculated load which means that my #12 wire is too small?
My AHJ is also saying that I must apply the 125% (80%) rule to the derated ampacity, ie 14.1 x .8= 11.28Amps is all that my #12 wire is allowed to carry?
and last, if I must upsize my 2 #12 CCC to #10, may I leave the Neutral and EGC at #12?
Thanks for any replies
I have an ambient temp of 26-30C and an addr for rooftop of 33degC= 63deg C to enter T310.15 B 2 a
#12 has ampacity of 30A x .65=19.5Amps. this means I can have up to 19.5 calculated Amps running thru this wire, correct?
OR; becuause the #12 is termianted at the 75 deg switch, I must use the 75deg col. of T310.15 B 2 a, which has a factor of .47 x 30A = 14.1Amps of Ampacity, which is .3 amps less than my calculated load which means that my #12 wire is too small?
My AHJ is also saying that I must apply the 125% (80%) rule to the derated ampacity, ie 14.1 x .8= 11.28Amps is all that my #12 wire is allowed to carry?
and last, if I must upsize my 2 #12 CCC to #10, may I leave the Neutral and EGC at #12?
Thanks for any replies