encoreman
 - Austin, TX
I told my customer that I had to install a neutral to ground bond at the first disconnect after the meter which is on a pole 100 feet away from his small building. He wanted me to make the neutral to ground bond at the panel inside the building. I explained to him that it had to be at the disconnect because the local jurisdiction adopted the 2008 NEC.
He was not happy, but did not argue. I returned to the building several months later and found he had grounded the neutral at the panel. The ground at the panel connects to an extensive ground grid surrounding the building and has a physical copper underground connection to the ground at the disconnect. There is also an equipment ground wire from the disconnect to the panel.
I explained to him that he was in violation of the code and he could suffer liability damages if there was ever an incident that could be traced back to the illegal neutral to ground bond.
He wanted to know why the second neutral to ground bond could cause a problem. I did not have an answer that satisfied him.
Does anyone have an explanation as to what kind of problems he could experience? (electrical problems not legal problems). I told him I could not work on his premises until he rectified the problem. I suspect he will disconnect the neutral to ground before he calls me out and will reconnect it after I leave. I need a practical answer so he will leave the neutral to ground bond only at the disconnect.
Thanks!
Jack
Thanks!
Jack