Bonding bushings

Status
Not open for further replies.

101010

Senior Member
Paralleled service feeders that enter a trough before they enter the panel. Should there be a bonding bushing on the pipes entering the trough and the pipes entering the panel? or just the panel? in the panel only one pipe needs to have bonding bushing right?
 

JDB3

Senior Member
If there are NO eccentric or concentric knockouts, are bonding bushings or locknuts required? :? This still is confusing to me!:?:? Code article please. Thanks
 

JDB3

Senior Member
OK Dennis, but if it is for a residence 120/240 single phase, would they be required by code? One co-op in this area wants them on everything on a 320 amp service! :huh:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
OK Dennis, but if it is for a residence 120/240 single phase, would they be required by code? One co-op in this area wants them on everything on a 320 amp service! :huh:
You cannot fight the Utilities. If they want it then do it but the code does not require it necessarily. I have always seen bonding bushing used and in fact some reducing washers are listed for use for bonding.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
OK Dennis, but if it is for a residence 120/240 single phase, would they be required by code? One co-op in this area wants them on everything on a 320 amp service! :huh:
One end of all metallic service conduits require something other than standard locknuts to bond them. 250.92(B)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
All metallic raceways and enclosures containing service conductors must be bonded by one of the methods listed in 250.92(B).
Your pipes entering the trough can not depend on standard locknuts and bushings for bonding.
If all you are doing is bonding the raceway, then a accepted bonding means on either end of all raceways is is acceptable.
If you are depending on the raceways to bond the trough, then both ends of the raceway must have an acceptable bonding method.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
All metallic raceways and enclosures containing service conductors must be bonded by one of the methods listed in 250.92(B).
Your pipes entering the trough can not depend on standard locknuts and bushings for bonding.
If all you are doing is bonding the raceway, then a accepted bonding means on either end of all raceways is is acceptable.
If you are depending on the raceways to bond the trough, then both ends of the raceway must have an acceptable bonding method.

Much better explanation than I gave. :thumbsup:
 