On site we have a long run of 2 1/2" RMC containing three 3/0 thhn conductors with #4 AWG thhn Grd.
Due to the distance Quazite Boxes have been installed as Pull points.
Voltage is 480V 3ph.
I have instructed the contractor to install Bonding bushings on each conduit and connect (#4 AWG) or use Fiber Bushings and provide a acceptable and approved bonding jumper between conduits.
I reference NEC 250.96 NEC 250.97 NEC 344.46 and NEC 300.4G.
Is there any other articles that apply and/or do any of these not apply.
As for the #4 EGC.
It is my understanding that this can pass thru the pull points uninterrupted.
Is this correct?
FYI: Terminating to a distribution block and 60Amp Breaker (with compression reducers).
thanks.