You two keep resorting to the bonding being established through the wire EGC. 250.96(A) CLEARLY says with or without supplementary EGC, which includes the wire EGC. Without the wire EGC, the metal conduit run would serve as the EGC. That's what it means. You must install a run of metal conduit as if it is the only EGC. And where flexible conduits are not permitted to serve as an EGC, you have the same condition.
I am sure all of us have seen EMT couplings have come loose at which point there is NO effective ground fault current path. So, seeing that do we have to install the wire type EGC in a conduit? NO, so I don't think a mechanical continuity (for bonding purposes) is required unless it the sole EGC for the circuit.
You must install a run of metal conduit as if it is the only EGC. with the same token can we say. "every conduit must have a EGC wire type as if the couplings and connectors will be loose"
Just the way that I see it.