300.5 (D) (3) requires buried service conductors (not feeders or branch circuits) to be marked with a 'warning ribbon'.
The definition of service kind of says that service conductors are POCO conductors, so the NEC wouldn't apply.
I just watched the POCO do a buried run to a meter socket and they didn't put tape in it. I was talking to one of the linesmen about it and he said that the NEC didn't apply to service wiring.
So, just where would be a place that this rule would actually apply?
NEC or not, not putting in a tape is just plain moronic. Not putting it in correctly is equally idiotic.
It would apply any place good installation practice trumps idiocy. Not much you can do if the POCO supplies the ditch and the wire. However, plenty of UG service laterals are ditched and installed by the owner - maybe the last few feet is by the POCO. Being the NEC mentions it twice, and the work is by an NEC journeyman, I'd say it applies.
It applies here, because the poco won't pull the wire thru the conduit until the Poco engineer stamps an approval, and he won't do that until you invite him to come watch you backfill the trench and put the marking tape in a foot from the top of the trench. Backhoe operators are not thrilled with this as you can well guess.........
In my humble, minute, and mini opinion, it got into code because the persons on that cmp were confused on the subject themselves. (nah, that couldn't possibly happen could it?)
The percentage of stupid: backhoe operators, electricians, ECs, and engineers; appears to be uniform through out the earth. Most every job I've been on the spec is: the tape is between 12" and 6" of finished grade. An unhappy backhoe operator doesn't make the list of concerns.
In my humble, minute, and mini opinion, it got into code because there are ECs that dump in the wire, throw in the tape, and then backfill. Disgustingly stupid. So, I think this is one thing the CMP got right.
ice