Greetings,
I have a 1000/1333 kva fan cooled transformer 8 % impedance. Primary voltage is 4160, secondary is 480/277. My question is this: The transformer should deliver approximately 1600 amps at full load if the fans are operational ( which I am not sure if they are). If the fans are not operational does that limit my transformer to the 1000 kva stamp? This would give me approximately 1200 amps. My next question concerns a power factor that averages 90%. Does this also derate my kva?
Thank you for your help
I have a 1000/1333 kva fan cooled transformer 8 % impedance. Primary voltage is 4160, secondary is 480/277. My question is this: The transformer should deliver approximately 1600 amps at full load if the fans are operational ( which I am not sure if they are). If the fans are not operational does that limit my transformer to the 1000 kva stamp? This would give me approximately 1200 amps. My next question concerns a power factor that averages 90%. Does this also derate my kva?