Derating wires in conduit.

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with Fuel, 310.15(B)(3)(a) does not consider vertical VS horizontal nor continuous VS non-continuous.

Chris
 

G._S._Ohm

Senior Member
Location
DC area
A vertical conduit may have convection air currents which should make some difference, but evidently too small for NEC purposes.
 
derate

derate

Thank You for the replies.Was thinking without a continious load there would be less heat build up also with vertical conduit the
wire is not laying in bottom,less heat.The installation has a 2 inch conduit,33 inches long.Has 6# 10,2#8 and 4# 12
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thank You for the replies.Was thinking without a continious load there would be less heat build up also with vertical conduit the
wire is not laying in bottom,less heat.The installation has a 2 inch conduit,33 inches long.Has 6# 10,2#8 and 4# 12
I understand your thinking on this but the NEC has never approached it since it would be hard to know if the conduit wouldn't have conductors clumped to one side or not.
 

jusme123

Senior Member
Location
NY
Occupation
JW
Thank You for the replies.Was thinking without a continious load there would be less heat build up also with vertical conduit the
wire is not laying in bottom,less heat.The installation has a 2 inch conduit,33 inches long.Has 6# 10,2#8 and 4# 12

Conduit size is not a factor when derating, these same conductors you have listed above could be installed in a 4" conduit, the derating will be exactly the same.
 