Hi Mike:
I have a question about NEC 240.86.
My question is about the series rating of MCBs in series with current limiting fuses. UL has published a number of tables for acceptable series rating combinations of current limiting fuses and MCBs. NEC 240.86 says that the series rating of a breaker/breaker series combination can not be used if the motor contribution to the bus between the current the upstream protective device and the protected MCB is greater than 1% of the interrupting rating of the MCB. I don't understand the logic here.
If UL has tables of tested fuse/MCB acceptable series combination don't they still apply to the fuse/MCB combination. I understand those tables to say that the downstream MCB remains passive while the current limiting fuse interrupts the SC current. If the motor contribution, which I understand will continue to flow after the fuse has interrupted the main system contribution, is less than the interrupting rating of the breaker (which will interrupt the motor contribution) why can't I use the series ration of the fuse/MCB combination?
Thanks for your help.
Tom McCauley
Tom McCauley