At a job site there are two cooling tower pump motors. in the past year one has failed twice and the other once.
Input voltage to VFD is a steady 480-482. At the disconnect with it being off the voltage reads are puzzeling. With a Fluke
meter the one that has the u shape to go around the wire the voltage reads 480 volts. With a better Fluke and a Greenlee
the voltage reads 530 -570 volts.
It seems the cheaper meter reads 480 while the better reads higher. Is there an explanation for this and could the VFD not be
set up properly for these particular motors ? The VFD'S are ABB'S