RAM1of4
- NW Missouri
Scenario (generalized): A new Solar PV system to be installed. Main panel has 200A bus and breaker. PV backfed breaker to be 70A for load-side connection to bus. Design shows main breaker to be derated to 150A in order to stay below 120% of bus rating...(150+70=220A<240A).
Me: I feel the contractor needs to perform load calculations to verify the remaining loads will be properly served with the derated main.
Electrician: Providing calcs is excessive and unnecessary. The system will simply be safer with reduced main breaker capacity. Worst-case scenario is that the customer may experience nuisance tripping.
I think the reasoning is absurd and absolutely clear that a little professional responsibility should be afforded to the customer. Regardless, I prefer to have black and white references to back up my reasoning as opposed to pushing my weight around just because I can.
QUESTION: Does the NEC require that load calculations be performed to ensure proper sizing of the main breaker for purposes of derating?
Thank you,
RAM
Thank you,