new job starting soon,
Its a 3 storie hotel, with a 100 rooms
wood frame tgi and truss
each room needs 5- 20 amp ckts,
2 for lights 1 for p-tack 1 for gfci and 2 for outlets
33 rooms per floor
No cooking
each room must have a "master lighting disconnect switch"
Looking for the best answer for mc cable.
I would like to cut down the number of homeruns from 160
to avoid a huge bundle/ derateing above main hallway ceilings
back to panel room
If i run 2- 12/3's and 1-12/2 per room
with 2-2p 20 amp breakers and 1 1p breaker
adding time pigtailing the grounded conductor
0r run 2-12/4's and 1-12/2 per room with no time adding the tails
and have choice of breakers 1p or 2p seeing that i an not shareing a grounded conductor
landing each conductor of the same cable on the same phase hence not a true multiwire branch ckt
or am i bound to use a breaker tie for all for poles with the use of 12/4 mc cable?
And yes i would have liked to pipe back to Mech room meaning more fun derateing and time
At the job meeting today ( unable to make)
AHj inspector called for today Arc faults that will be tomorrows battle of 210.12
what would you do?
33 rooms per floor
No cooking
back to panel room
what would you do?