JJspark
- Denver, Co., U.S.A
where in the code is the table for jacketed cable such as Belden Foil?:blink:
It is type CMR ,#18awg. it is used for 4-20ma signal on transducers
I'm looking to find how to do pipefill with jacketed cable such as CMR.
So you don't have to worry about voltage drop.4-20ma signal
I also believe these cables are exempt from normal pipe fill rules. It is a matter of what you can fit and pull. If it is a straight run, may not be too hard. If you have some bends, you may want to stay within normal fill rules.
Can you cite the NEC Article for this alleged provision/exception?
take a look at 800.110 ('08 NEC) last sentence
That is not citing:lol:
4-20ma cable would be covered by Article 725, not 800.take a look at 800.110 ('08 NEC) last sentence
Whether the cable is subject to raceway fill rules or not, I would still want to take into consideration just how full the raceway is going to be and how hard it may pull. No point in running a particular raceway size at all if the total area of cables to be pulled through is larger than the raceway, but I still think I would want only near 40% fill for ease of installation purposes than to jam it as full as possible.