Jacketed cable (Belden)
What is this cable used for? I doubt the nec will address the cable by the brand. Is it communication cable? alarm? What are the letters of the cable?
I also believe these cables are exempt from normal pipe fill rules. It is a matter of what you can fit and pull. If it is a straight run, may not be too hard. If you have some bends, you may want to stay within normal fill rules.
That is not citing:lol:
Plus, it only applies to communications circuits.
"voice, audio, video, data, interactive services, telegraph (except radio), blah, blah blah" and includes outside wiring (not inside) for alarms.
It does not apply to the cable itself. If the cable is used outside the scope of Article 800, the fill requirements still apply. For example, if they were used for remote control, signalling or power limited circuits, they would not be exempt from fill requirements.
I guess it way my error mentioning Art. 800 in the first place. Yes, the cable is covered there, but in this case we need to follow 725.
Throwing 800 in seems to have caused a distraction. Sorry.
Whether the cable is subject to raceway fill rules or not, I would still want to take into consideration just how full the raceway is going to be and how hard it may pull. No point in running a particular raceway size at all if the total area of cables to be pulled through is larger than the raceway, but I still think I would want only near 40% fill for ease of installation purposes than to jam it as full as possible.
I don't know why 800 has the exemption, really it makes no sense.
How does the application (after the fact) determine fill? I don't see that anywhere else but 800.
I guess I started kind of a mess with the fill rules exception. I agree - if ignoring fill rules is fine for CM circuits, why not for NEC 725 circuits? The inspector may not know the application of the circuit. He can guess by the marking on the cable (CM -vs- CL2, but CM is a permitted substitute for CL2). I deal with many items that have a USB interface (switch panels, lighted displays, etc). We use a USB to Cat5 converter/extender and the in wall Cat5 with RJ45 wall plates to extend these back to a source controlling computer. One day, those in wall cat5's could be ethernet (communications) and another day USB remote control (NEC 725 maybe).
I think the differences between 725 and 800 are hard to reconcile many times. Am I communicating with a transducer (sending on/off data or reading its value), remote controlling a transducer, or is it a power limited circuit? From reading the scope of 725, it seems to apply when you're building a control circuit from discrete things -- a CL2 power source, a switch, a doorbell, a relay, maybe a transducer. Although most communications interfaces are inherently power limited, they are generally not labeled as a power limited CL2/CL3 power source unless there is some CL2 wall wart that powers the whole thing. I think only a circuit which uses a CL2/CL3 power supply and perhaps some other discrete items will put you into NEC 725. If you have some type of control box that isn't listed as a power limited supply, which then has some external low voltage low current wires which goes to some item, I'm not so sure NEC 725 applies.
Finally, CL2 and CM cables are permitted to share the same raceways. If you mix, whose fill rules do we use -- 725 or 800?
Damn, the rest of us have been running raceways without considering if the conductors would fit. :D.