Damn, the rest of us have been running raceways without considering if the conductors would fit..
Well, I may have overstated the obvious when it comes to more cable than you have raceway for, but even when following the 40% fill rules for power conductors, I have had plenty of 40% or less filled raceways that have pulled pretty hard. So I would think if I had similar fill with communications I still would not want more than 40% fill on a long pull or one with three or four 90 deg bends