It would be safer only in the context of the connection being two terminations closer to the source. Safeness is dependent on where the fault occurs. If it occurs somewhere other than at or between these two terminations, essentially no difference.Would it be safer for a plumber/homeowner if I were to move the GEC from the sub panel to the disconnect in the meter pedestal? The end result would be the GEC connected to the grounded conductor terminal at the disconnect and then terminated to the galvanized piping in the house probably down by the meter where the supply from the city enters the basement. Thoughts?
I believe it is compliant as it is now for existing installations. If you relocate as suggested, it's my opinion you would also have to run an EGC to the subpanel and isolate its grounded conductors and EGC's. Where's the MBJ?