solarama
New member
- Location
- Santa Rosa, Sonoma, CA
We installed a small (30 module) system on a commercial building, to supply power to the parking garage, whose bill is paid by the owner. An existing 100 amp load center serves the garage and is supplied by a 40 amp main, and has its own meter. We brought the source feeder from the roof to a 30 amp fused disconnect (with 20 amp fuses), located adjacent the load center, and with a splice can between them. We brought #2 copper in a new conduit from the service main to the splice can. We resupplied the load center with #2, and made a #6 tap to the fused disconnect with 4 feet of wire. In my opinion this conforms with the requirement in 690.64 that "each source be interconnected at a dedicated circuit breaker or fusible disconnect". The inspector took exception, claiming the "point of interconnection" is the tap, not the fused disconnect, and wants instead for us to provide another panel subfed from the existing to provide space for a circuit breaker to land our source circuit. My position is that the tapped disconnect is simply a way of extending the bussing of the load center, and is no different from what he wants. I believe the key word is "dedicated", meaning that one should not combine more than one source at a splice or tap, before landing them at the disconnecting means. Think of it this way: If one had a gutter, with 100 amp rated conductors, and three fused disconnects serving three loads, each tapped from the gutter, then added our source circuit from our disconnect at a tap in the gutter, would this not comply with the code?