tallgirl
- Glendale, WI
- Controls Systems firmware engineer
That doesn't mean those installations are truly compliant. It just means those AHJ are either unaware of the violation or simply choose to ignore it... take your pick... but I certainly would not take any action to make them aware either.![]()
I'm still not convinced the install isn't compliant. And just because the code seems to be fairly silent on a point doesn't mean something is forbidden.
Power conversion equipment is inherently current-limited, both by the amount of available input power (PV or whatever) and by the design of the equipment. Presumably the lab doing the testing has verified that the device won't exceed its rated output -- I have clients who do bad designs (... because they don't listen to me ...) and even they can't exceed (by much) the rated output of the equipment they install. So, that rules out the situation with some inverter going nutso and violating several laws of thermodynamics on the supply side.
Then you've got the issue, as was raised, that a UL1741 certified inverter CANNOT feed a short. Heck, they can barely feed overloads if they cause significant voltage drop at the inverter terminals. This is definitely tested for UL1741 certification and the response times are faster than many trip curves -- which is its own set of problems (inverters that trip out too fast when presented with a surge).
The only scenario that can lead to any problem is one in which an inverter suddenly presents a load that is "large", but not a bolted short. The flip side -- an inverter suddenly producing more power out than it receives as power in is ruled out by the First Law of Thermodynamics.