I was watching Mike Holmes, episode "Pain in the glass" at DIY channel, and in the episode the electrician said that the panel can't be mounted in vertical position because he state that the branch circuit wires can't be run from top of the interior panel, because line and load wires can't be mixed together next to the main C.B., My question is if manufacture instructions allows you to do this then I don't see any code violation.
To fix the problem in the episode they mount the panel in an horizontal position so branch circuit wires can be run to the side of the panel. Now this is a violation of the code article 240 section 81 indicating that C.B. shall clearly indicate whether they are in the open "off" position or closed "on" position, because the "up" position of the handle must be in the "on" position. The only code section I can find on this matter is 230.7 conductors other than service conductors shall not be installed in the same service raceway or service cable.
Comments will be appreciate.
thanks.
To fix the problem in the episode they mount the panel in an horizontal position so branch circuit wires can be run to the side of the panel. Now this is a violation of the code article 240 section 81 indicating that C.B. shall clearly indicate whether they are in the open "off" position or closed "on" position, because the "up" position of the handle must be in the "on" position. The only code section I can find on this matter is 230.7 conductors other than service conductors shall not be installed in the same service raceway or service cable.