seperatly derived system

Status
Not open for further replies.

AZJoe

Member
Location
Marana,AZ,US.
Hello;
277/480 3ph grounded system with no neutral loads served,system is grounded and bonded at first disconnect, EGC taken to secondary XFMR with secondary XFMR 480/120-240, if secondary XFMR is grounded and bonded seperatly wont this create multiple ground fault paths for original system between the two grounding electrodes. Can the secondary neutral just be bonded to primary EGC.
Thank You: AZJoe
 

raider1

Senior Member
Staff member
Location
Logan, Utah
No.

Keep in mind the fault current wants to require to the source. The transformer is the source where the fault current from the secondary want to return to not the utility transformer.

Hope this makes sense.

Chris
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Hello;
277/480 3ph grounded system with no neutral loads served,system is grounded and bonded at first disconnect, EGC taken to secondary XFMR with secondary XFMR 480/120-240, if secondary XFMR is grounded and bonded seperatly wont this create multiple ground fault paths for original system between the two grounding electrodes. Can the secondary neutral just be bonded to primary EGC.
Thank You: AZJoe
Multiple paths between grounding electrodes is not an issue. The issue is when you have multiple paths from a grounded conductor to earth. The grounded conductor of the 480/277Y system and the grounded condutor of the 120/240 volt system are not the same grounded conductor. Both must be connected to earth at a single location.
You are not permitted to use the primary EGC as the secondary grounding electrode conductor, but there will be a physical path between the primary EGC and the secondary grounded conductor in a code compliant installation.
 

Smart $

Esteemed Member
Location
Ohio
.... Can the secondary neutral just be bonded to primary EGC.
Thank You: AZJoe
The secondary neutral is required to be bonded to the nearest of water pipe or structural steel electrodes. If neither of those exist in the building or structure, the neutral must be connected to the building or structure grounding electrode system.
 