Ok I am a little confused with 376.23. I have a CT cabinet and Enclosed Circuit Breaker and i would like to lay an 8 x 8 wire way across the top to run (8) 350 Kcmill copper conductors. I am unsure if the code would consider this a U pull per 376.23 (b) which would make my cable entries be no less than 21" apart considering 3.5" conduit for the (8) THHN 350 and it would require the trough to also be at least 24.5" high. Is my understanding correct?
My other thought says that this is not a pull box senario and 376.23 (b) does not apply and that 376.23 (a) does and the i should be fine with a 5" clearance from the cable entry to the opposing side of the trough.
What are you thoughts?
My other thought says that this is not a pull box senario and 376.23 (b) does not apply and that 376.23 (a) does and the i should be fine with a 5" clearance from the cable entry to the opposing side of the trough.
What are you thoughts?