Vertical Riser Cable Support - another question

Status
Not open for further replies.
There are two #10 THHN stranded conductors in a 1 inch rigid conduit. The installation requires a Vertical Riser Cable support. None of the manufacturers seem to make a device for such a small pipe and conductors. Some electricians tie a knot in the conductors at the top fitting. What do you do?
 
Thanks for the response Ron,


I see in the link that the minimum cable size is 0.5" diameter. However, two #10 THHN are (0.164" diameter X 2 conductors) 0.328" and there is no outer cable over the slippery nylon to provide something for the metal net to grip.

Perhaps there are not enough towers for a company to make a support this small. Oh, wait - I forgot about all of the cell towers, water towers, television and radio towers...hmm...perhaps I should invent something.

What does the code say about using a device that is not NRTL listed or labeled in this application? (My CD rom is broken and my paper code is out of date...)
 