I was reading over the voltage drop publication seen here: http://www.mikeholt.com/technical.php?id=technicalvoltagedrop1
Midway down the page after the first example is this:
"Author?s Comment: The 5.3% voltage drop for the above branch circuit exceeds the NEC?s recommendations of 3%, but it does not violate the NEC unless the 16 ampere load is rated less than 113.6 volts [110-3(b)]."
This example was in reference to a 120V rated load. So, the author is saying that if the load was rated for 110V, it would violate the NEC?
Or for a motor rated 460V, if your calculation says the voltage drop from a 480V source would give 465V at the motor terminals, you are violating the NEC according to the author's statement...
That just doesn't make sense to me. One, it is a calculation and two, voltage varies throughout the day.
Also, I believe he was intending to reference NEC 110.4, but I'm not sure.