mark32
Senior Member
- Location
- Currently in NJ
A few months ago I installed a transfer panel for a portable generator. (To help visualize this arrangement, I put this panel next to the main panel in which I reused an existing 100a breaker that was feeding an existing sub panel elsewhere in the house) When I re-energized the new panel I heard a sizzling coming from the existing Siemens or BR 100a breaker. When I removed it it was easy to see it had been arcing. I stuck a small flat head screwdriver into the part that pushes onto the buss and it was very weak, it had no strength left to it. I replaced it later in the day but a few thoughts entered my mind as to what caused this failure in the first place.
First thought, I, and most everyone I know, terminate a majority of breakers (All push on breakers by the way) once they are in the panel. I think by torquing the termination I/we are putting some stress on the tang that conforms to the buss.
Second thought, This breaker had #2 cu terminated to it and being a rather stout conductor, it possibly put continuous stress on those tangs, especially when you consider this breaker had not a breaker on either side of it.
Any thoughts?
First thought, I, and most everyone I know, terminate a majority of breakers (All push on breakers by the way) once they are in the panel. I think by torquing the termination I/we are putting some stress on the tang that conforms to the buss.
Second thought, This breaker had #2 cu terminated to it and being a rather stout conductor, it possibly put continuous stress on those tangs, especially when you consider this breaker had not a breaker on either side of it.