TrickleCharge
Member
- Location
- CA
Ok so I have a project where they are adding an EV charging station and the original panel load was 124A on a 100A panel. When I sent the correction back the response I got from the contractor (who does solar) said "I am allowed to go 120% of the rating. I laughed under my breath and said that did not apply. Well anyways they submitted a new revised load calc that just so happens to come in at 99A, seems like they are just "making it work". They use a cheesy spreadsheat that calculates the circuits in amps. There are some receptacle loads, RTU, and a few other pieces of equipment on this panel (maybe 8 ckts). The EVCS draws 32A/Phase as shown on their panel schedule. Now because they are being difficult with providing accurate calcs that are "true" can I request them to meter this panel per 220.87? What do you guys think?
Thanks