gfdbiker
- Cincinnati, OH
I' have been reading all day on NEC 695 and my brain is getting mushy. I need some assistance in my intepretation. I have a new building being installed on a campus. It's being fed by 2- 13.8kv feeders from distribution gear in another building each from a different utility source. The 13.8 feeders travel approximately 150' through adjacent mechanical rooms were they terminate on a fusible disconnect switches on the transformer primaries. We are planning on tapping the secondary of both sides of a 13.8kv- 480v 2000kva double ended sub for the two feeder sources for the fire pump. The tap will be in it's own section before the main 480v breaker. Each tap would terminate in seperate disconnect with OCPD rated for locked rotor current located in the same electric room approximately 30' away. The fire pump is in an adjacent room. Both rooms are 1hr fire rated.
My questions are:
Does the primary side of each transformer need to be outside the building since it's a feeder not a service entrance(ie under the slab) or be 2 hour rated? My interpetation is no although it may be a wise thing to do.
Does the cable from the tap on the transformer secondary to the OCPD have to be "outside the building"(ie under the slab) or concrete encased? - My interpetation is yes
Does the feeder from the OCPD to the fire pump transfer/ controller have to be 2 hr rated since the fire pump room is adjacent to the electric room?
Can the 2 OCPD devices be in seperate but adjacent enclosures?
Thanks in advance
My questions are:
Thanks in advance