scotteng
Member
- Location
- Apollo Beach, FL
- Occupation
- Professional Engineer
We design a chain of banks in Florida that utilizes a manual transfer switch (MTS) with camlocks for connecting a portable generator. The MTS is mounted on a freestanding structure next to, and downstream of, the utility meter. The location of the MTS support structure varies and can be near the building or somewhat distant. The MTS contains the service main disconnect and as such, we ground and bond the service neutral at this point. An EG is then run with the feeder conductors from the MTS to the building main panel, which also contains a main disconnect for the building. The building gets a pair of ground rods and all available grounding electrodes at the building are tied together and bonded to the EG, but NOT to the neutral. We are treating this as a building supplied by a feeder per 250.32.
An field inspector has given us a comment that we need to tie the ground rod at the MTS to the grounding electrode system of the building with a separate GEC. He is stating that the design we show utilizes the EG that is run with the feeder as a GEC, which is prohibited. I see this as one building fed from another which does not require a separate GEC run between buildings. Thoughts? Is there a minimum distance where the ground rods are close enough that they should be tied together?
An field inspector has given us a comment that we need to tie the ground rod at the MTS to the grounding electrode system of the building with a separate GEC. He is stating that the design we show utilizes the EG that is run with the feeder as a GEC, which is prohibited. I see this as one building fed from another which does not require a separate GEC run between buildings. Thoughts? Is there a minimum distance where the ground rods are close enough that they should be tied together?