A building was originally constructed as a multi-tenant building with several services. A single client has gradually acquired all the spaces for a mission critical call center. The current project is to replace an existing 208/120Y service with a 480/277Y service to mirror an existing 480/277Y service for a UPS system. From the existing transformer, there are two existing services. One, a single mcb panel which has very little load will be fed from another existing panel. the other is a 4-stack meter base which will be replaced by a single meter and 480/277Y panel. This new panel will feed transformers for the existing 208/120Y panels.
Since building already has several services (at least 7 for the part I'm involved with) due to its original construction, and we are only replacing existing services (actually reducing 5 metered services to two) with new of a different voltage. and since this is a call center, is this allowable under 230.2(A)(6) or (B)(1)? I'm trying to make my case with the plan reviewer. Looking for others feedback or opinions who might have encountered similar situations.