I would have assumed a garage classified as a "minor repair garage" would be less strict than a "major repair garage". Lets consider 2 senarios where there is an un-ventilated pit in the garage and there is no gases such as hydrogen and there is no dispensing or transferring of flamable liquids (diesel repair facility) with a flash point below 100 degree F.
If in a Minor Repair Garage, the pit area would be a class 1 Div 2 area. This is because 511.3(D) says D.1, D.2, and D.3 are applicable.
However, if the garage is a Major Repair Garage, the pit area would be unclassified. This is because 511.3(C) says C.1, C.2, C.3, are only applicable if the transfer of the flammable fluids / gasses. Since no flammable fluids or gasses, don't need to follow the pit classification area.
Am I missing something here?
If in a Minor Repair Garage, the pit area would be a class 1 Div 2 area. This is because 511.3(D) says D.1, D.2, and D.3 are applicable.
However, if the garage is a Major Repair Garage, the pit area would be unclassified. This is because 511.3(C) says C.1, C.2, C.3, are only applicable if the transfer of the flammable fluids / gasses. Since no flammable fluids or gasses, don't need to follow the pit classification area.
Am I missing something here?