Point of interconnection to 3phase, 4wire EDC

Status
Not open for further replies.

UMirza

Member
Location
Newyork
Hi,
"Can you please explain in detail what this means and how to draw it on paper.
When a customer-generator facility is to be connected to 3 phase, 4 wire primary EDC distribution lines, a 3 phase or single phase generator will be connected line-to-neutral and will be effectively grounded."
fyi-We have conductors tapped on each phase and neutral bonded to neutral and ground conductor to building steel.
Thank You

Usman
 
Hi,
"Can you please explain in detail what this means and how to draw it on paper.
When a customer-generator facility is to be connected to 3 phase, 4 wire primary EDC distribution lines, a 3 phase or single phase generator will be connected line-to-neutral and will be effectively grounded."
fyi-We have conductors tapped on each phase and neutral bonded to neutral and ground conductor to building steel.
Thank You

Usman
Welcome to the forum(s) :thumbsup:

I think you may have misplaced ".

Can you provide more context?

I believe this is simply saying the generator must be configured for grounded-neutral wye output. I assume by drawing you mean one-line diagram. Simply annotate the generator symbol with voltage configuration and put a grounded-neutral wye symbol next to it.
 