San -Brooke
- USA
Not only that but the CBs on the right do not look like GE they look more like Sq D OQ/QOB's?
Who installed this CB Stevie Wonder?
View attachment 7954 This may help for you to see how it was possible
Picture with no dead front would have been nice. I well understand a breaker with lugs on each side, but how did they connect to the bus?
I guess if it were a panel designed for bolt on breakers, you could bolt a jumper to the bus to feed the breaker, assuming there is clearance for everything to fit, maybe the breaker had more clearance on one side than the other and why it is mounted the way it is.
I don't see a violation here as far as the handle operating the opposite direction from the other breakers. If it operated vertically then handle down would be required to be the open position. If I were to cite any code that is in violation, all that comes to mind is maybe 110.3(B)
Maintenance fixed it while I continued on with the inspection then I returned when it was fixed to verify. I would say it was more a safety issue rather than a violation. I envisioned someone needing to turn off circuits in haste and assuming everything would be de-energized. I tried to get a picture off the net of a panel but I could not find one. Basically the bus extends up at every circuit to land much like a wire at every breaker if I recall. I am just glad that no one makes them like that anymore. Sorry if that description does not give you a clear picture but I have slept a whole lot since I saw this.
So you are saying all the breakers in this panel are of the type with lugs on line and load side - makes much more sense that it would be easy to have one in a reversed orientation if that is true.
I remember installing bolt-on CB's in old panels that the CB could be installed either way, ON/left or ON/right. The breaker had screws at both ends and the bus had a fork connection to go around the screw. Some guys would install all of the left side CB's to be ON/right and all of the right side to be ON/left (a modern configuration). Others would use a combination of both which could be confusing. :blink:
Definitely not Square D (no trip window). Looks more like a Murray or Bryant, but the GE should have fit. Would love to see how they modified it to fit the buss though! (If it was actually working)