 - New Jersey
 - Journeyman Electrician (retired)
314.28(A)(3) Smaller Dimensions.Boxes or conduit bodies of dimensions less than those required in (A)(1)and(A)(2) shall be permitted for installations of combinations of conductors etc.The operative word being SHALL
So what are you saying?
Also you have only used half of the sentence, you left out "that are less than the maximum conduit or tubing fill (of conduits or tubing being used) permitted by Table 1 of Chapter 9, provided the box or conduit body has been listed for, and is permanently marked with, the maximum number and maximum size of conductors permitted."