bobbymari

Senior Member
Location
los angeles ca
Just had a rough inspection on a small commercial job. Inspector stated a new code was introduced requiring handelties on all breakers where it is a 3 wire circuit. Has anyone heard of this I still have the 2008 code book and he didnt have his book either.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Just had a rough inspection on a small commercial job. Inspector stated a new code was introduced requiring handelties on all breakers where it is a 3 wire circuit. Has anyone heard of this I still have the 2008 code book and he didnt have his book either.
Yep all circuits on a multiwire branch circuit must be able to be disconnected simultaneously. 210.4
 

LEO2854

Esteemed Member
Location
Ma
Just had a rough inspection on a small commercial job. Inspector stated a new code was introduced requiring handelties on all breakers where it is a 3 wire circuit. Has anyone heard of this I still have the 2008 code book and he didnt have his book either.

Either that or two pole breakers.
 