a trans. has a rated pri. current of 90 amperes at 480v. what is the maximum rateing permitted for primary overcurrent protection if secondary overcurrent protection is ommitted
from table 450.3(b) current over 9 amps. 90x125%=112.5. no such breaker size, so next higher one is 125amp.from 240.6.