rookie4now
Why do transformers have a marking that says "Keep all wires below this line?" The only thing I can think of is heat, but if you came in high and routed the wires properly it doesn't seem like that should matter.
I can't recall that warning being included on any transformers that I have sold over the years.
You must not have sold any dry type transformers between 30 and 300 kva because the vast majority have that label.
Interesting. I worked for Westinghouse as well as another dry type transformer manufacturer that manufactured transformers from the ventilated baby ones of 30kva up to 10mva and during my tenure with either manufacturer there was no signage such as the one described and to be an issue. I have transformers on the island of Guam, Saudi Arabia, Trinidad, Australia, and in many of the US states so I've sold a transformer or two, 2ph-3ph, 3ph-2ph, 3ph-1ph, in all sorts of enclosures. I even have a couple of transformers on an oil rig on the east coast of Africa and had one customer who wanted a 1500kva core and coil only designed such that it could be installed in a nitrogen filled TENV enclosure that they would be fabricating themselves which I had shipped to Australia.
Yes, I've have my share of transformers and No, since entering this industry in 1982 I have never recall such signage on a transformer and it has never been brought up as being an issue. There have have been some markings that directed the installer to enter and exit the enclosure in certain areas however for structural reasons such as obstructions.
Same here. I will admit that I have seen some without a line but that is the exception not the norm.We install tons of transformers of different brands and the overwellming majority will have stickers inside that say things like 'No field entry above this point' or 'Conductors must remain below'. Etc.
No disrespect intended but how many of these have you had your eyeballs inside of?