NEC 517.14 Panelboard Bonding:  The equipment grounding terminal buses of the normal and essential branch-circuit panelboards serving the same individual patient vicinity shall be bonded together with an insulated continuous copper conductor not smaller than 10 AWG.  .....
Does the bonding wire need to be in conduit, or can it be ran without conduit?
If the answer is that it needs conduit, could it be MC or AC cable with a grounding conductor??