mstrlucky74
Senior Member
- Location
- NJ
If you were running one horizontal 500MCM MC feeder cable would you always need to rack(unistrut) it to support it or is there another method...straps
dunce
...probably too big for straps though. Thanks.
MC would need support per 330.30. If it doesn't run contrary to 330.12, I don't see why it can't be supported by and secured to a slab.
If you are talking Cu, you are looking at 5 lbs or better per foot so you need to keep that in mind when supporting.