Following are three methods to use if a clamp-on power meter is unavailable!
1) Load-Factor Estimate by Thermometer.
Where available, remove lifting-eye from motor carcass, fill hole with oil, insert old-fashioned thermometer. If a lift-eye hole is unavailable build a temporary reservoir with putty, or other suitable material, add oil, then insert thermometer. Load-factor, LF, is the ratio of measured temp-rise, Tm, to rated temp-rise, Tr, Then compare Temp-rise above ambient to the nameplate rating!
2) Load-Factor Estimate by Resistance.
Determine stator-winding resistance for "hot" and "cold" conditions. Load-factor, LF, is the ratio of measured Th to Tr. Then, for copper and aluminum windings:
Th = (Rh / Rc) x (Km + Ta) - Km. Since,
Tm = Th - Ta, then solving for LF,
LF = Tm / Tr = (Th - Ta) / Tr, yielding,
= (Kr - 1) x (Km + Ta) / Tr, where,
Ta = ambient temp when motor is 'cold'.
Th = ambient temp when motor is 'hot'.
Tr = motor's rated temperature-rise.
Kr = Hot to cold resistance ratio = Rh / Ra.
Km = Material constant, Cu=234.5 & Al=228.
Rh = Stator ?hot? resistance, Ohms.
Ra = Stator ?cold?resistance, Ohms.
3) Load-Factor Estimate by Slip.
If an rpm meter is unavailable (and the location is unclassified, or determined to be non-hazardous) use a Strobe-light. If a strobe is unavailable, use a fluorescent-lamp connected to the same supply as the motor's. It is now a "strobe" light.
The resultant shaft image will appear to slowly rotate backwards. Count the number of
rotations for one minute, and divide it by the number of poles to obtain actual slip. Then, calculate the ratio of actual to design slip. Multiply design Hp or kW by this ratio to determine actual output.
Note: The count is divided by the number of poles because the number of lamp flashes is usually (but, not always) 2 x line frequency!
Caveat: none of the above metods will be as adequate as a power measurement, but you will be able to calculate kW or Hp, kVA, and PF, more accuratly than with an ammeter!
Regards, Phil Corso