Metal objects located withing five feet of pool must be bonded to the pool equipotential grid NEC 680.26 B3. I failed an inspection just because a frame door is located withing 5 feet of pool, now the inspector want me to bond the metal frame of door to the pool grid, my question is, can I just bond the door frame by using a #8 solid copper wire and connecte it to the pool panel grounding bar? 
 The metal parts required to be bonded per 
680.26(B)  include all metal parts of electrical equipment associated with the  water-circulating system of the pool, all metal parts of the pool  structure, and all fixed metal parts, which include conduit and piping,  metal door frames, and metal window frames, within 5 ft of the inside  walls of the pool and not separated by a permanent barrier. Other  examples of fixed metal parts covered by this requirement include metal  fences and metal awnings. The bonding of these parts can be accomplished  by one or more of the following methods using a solid 8 AWG or larger,  insulated, covered, or bare copper conductor:  
  
  ?
		
		
	
	
Connecting the parts directly to each other in series or parallel configurations  
  
  ?
Connecting  the parts to the unencapsulated structural metal forming the shell of a  conductive pool or connecting the parts to a copper conductor grid  system used around the contour of a conductive pool shell  
  
  ?
Connecting the parts together using the pool shell constructed of bolted or welded steel as a common connection point.  
  
  ?
Connecting  the parts to the perimeter bonding grid consisting of either structural  reinforcing steel (rebar or welded wire mesh) or a solid 8 AWG bare  copper conductor encircling the perimeter of the pool  
  
  
No would be your answer.
Thank you