squeirdo
Member
- Location
- Santa Fe, NM 87544
We are submitting gear for a project that will operate at 480v nominal at 7500 ft. The specs require 600v rated breakers because 480v breakers can't handle 480v when derated for altitude. The one-line shows 38000A of available fault current at 480v. The breakers we have submitted have an AIC rating of 65000A at 480v. They are being rejected because they are only rated for 25000A at 600v. It looks to me like they are derating the 480v AIC of the breakers by a factor greater than .58 for the nominal system voltage. Does this seem right? Neither voltage and ampacity of these breakers would be derated more than .95 for this altitude. Why would such a high derating factor be applied to the AIC rating?