J john2mcc Member Feb 12, 2013 #1 is there a code that states which type of breaker is required depending on whether it is bolt in or snap in?
is there a code that states which type of breaker is required depending on whether it is bolt in or snap in?
LEO2854 Esteemed Member Location Ma Feb 12, 2013 #2 john2mcc said: is there a code that states which type of breaker is required depending on whether it is bolt in or snap in? Click to expand... I don't think that is in the code.
john2mcc said: is there a code that states which type of breaker is required depending on whether it is bolt in or snap in? Click to expand... I don't think that is in the code.
H hillbilly1 Senior Member Location North Georgia mountains Occupation Owner/electrical contractor Feb 12, 2013 #3 I think it has more to do with the AIC rating, even though bolt in breakers can have low AIC ratings, you usually do not see plug in breakers with higher AIC ratings.
I think it has more to do with the AIC rating, even though bolt in breakers can have low AIC ratings, you usually do not see plug in breakers with higher AIC ratings.