Feeder Or Service ?
Is the wiring going from an portable generator to a manual transfer switch considered service conductors or feeder conductors ? Is NM cable permissable for this installation?
FRom the generator would be a feeder. (see definition of a "service")
Is your plan to install NM to the portable generator itself or to a inlet ?
I see no reason NM could not be used provided it met all the standard requirements. (What you describe is a fairly common install locally other than it normally terminates in a generator inlet box)
I can invision NM (romex) strung across the ground, in a storm, as not really being code compliant. Given the OP's profile I question the question.
From post 3, I assumed that would not be the case. I had the same thoughts in post 2.
Given the question, I question the profile :D