I am planning to upgrade a service panel. In the past I have always done this from a new wall so there were no issues with wires or getting to the circuits.
This time I need to replace an existing panel. I would like to pull the existing circuits out of the old box and move them to the new box however the wires are not long enough. I do not want to break into walls and find the first Jbox in the chain the replace the wire and the old service is in such poor shape that I do not want to use is as a subpanel.
This must come up all the time with service panel replacements or upgrades.
Question, how do you extend the individual circuits to get the extra 3 to 5 feet of wire to connect to the new service?
Your post gives me the impression that you have experience pretty much only with NEW construction service installation and wiring.
You state that you are going to upgrade the service. I assume from 60 or 100 amps to 200 amps. If this is the case than you will be replacing EVERYTHING. Weatherhead, service wire, meterpan, ground rods/wire, cold water bond wire, feeder wire, etc, etc, up to and including the panel.
In most every case, I've installed my new panel in the same spot as the old panel, and a majority of the existing circuits will reach their new respective destinations. As others have said, wire nutting extensions in the new panel will solve most "short" wires. If a cable or 2 doesn't reach the panel at all, I usually just install a JB above the new panel and extend from there.
Keep working space and clearances in mind. There have been those times when I find the existing panel over and behind the 275 gallon oil tank, etc.