- New Jersey
- Journeyman Electrician (retired)
Would one of these be required to be weatherproof whether or not the attachment plug cap is inserted if installed in a wet location?
I think they have a nema-3 rating. With or with out the cord cap.
But there not rated raintight when in use, that's the rub...........do they fall under the same requirement as other outside receptacles........
406.9(B)(2) Other Receptacles. All other receptacles installed in a
wet location shall comply with (B)(2)(a) or (B)(2)(b).
(a) A receptacle installed in a wet location, where the
product intended to be plugged into it is not attended while
in use, shall have an enclosure that is weatherproof with the
attachment plug cap inserted or removed.
(b) A receptacle installed in a wet location where the
product intended to be plugged into it will be attended
while in use (e.g., portable tools) shall have an enclosure
that is weatherproof when the attachment plug is removed.
That's the question.
Since it's not 15 or 20 amp then 406.9(B)(1) won't apply that sends you to 406.9(B)(2).
So is a portable generator a portable tool?
Even if it was considered as one, it would not be attended.![]()
Was recently brought up at my local elec cont meeting. It doesn't require an in-use cover as long as it is twist-lock. Local inspector showed the code section to me....don't have my book handy.
I'm skeptical.![]()
Does anyone have a code reference?
An inlet is not a receptacle. I don't see how that code section applies.
I agree 100%.
There is some logic in what you say here. Still don't have me convinced it is a receptacle. Can I just use a pigtail cord instead of the inlet? Now we get into whether the application is acceptable to use flexible cord. If we deem it is acceptable do we need a watertight cord cord connector and cap? I havn't ever seen a cord cap male end that is watertight when not plugged in.I thought about that too although it makes little sense because the intention is to prevent water from entering while in use. Is there a definition somewhere that says a receptacle is defined as being female only and would exclude something like in the photo in the OP?
I agree, an inlet is not a receptacle.
We also install a lot of 480v twistlock receptacles for chemigation at pivots. (Those big round circle things you guys see when flying over NE) We install with a standard wp cover on the bottom of a 3R enclosure. Facing down.
Definition of RECEPTACLE
1
: one that receives and contains something : container
2
[New Latin receptaculum, from Latin]
a : the end of the flower stalk upon which the floral organs are borne
b : a structure or tissue (as of a fungus or fern) bearing spores or sporangia
3
: a mounted female electrical fitting that contains the live parts of the circuit