112.5 KVA Transformer heat rejection
If temp rating of a transformer changes, its efficiency may also change. So if one knows efficiency, power factor etc of a transformer per OP and post #4, it is possible to calculate the heat rejection of the transformer using the following identity:
{(1-output/input)*[output/(output/input)]}=input-output...................(1)
Here input-output= losses of transformer=Heat rejection by transformer under steady state,
output/input=Efficiency of transformer,
output=KVA*Powerfactor.
Substituting values from post#4,
Output=112.5*0.9=101,25KW
Output/Input=0.95 on the left hand side of (1), the heat rejection is
(1-0.95)*(101.25/0.95)=5.33kJ/s or approximately 5 kW.
Take, for example, a dry type transformer. It operates at a higher temperature than an oil cooled transformer and so has a lower efficiency.
Whilst it is generally true that ONAN transformers are more efficient than dry types it isn't just a simple temperature difference. Core and coils differ between the two. Yes, i2R losses go up if you run at a higher temperature but they also go up if you reduce the cross sectional area of the conductor.
Here the discussion is about the OP choosing a transformer of particular temperature rating and so efficiency and not about design aspects of the transformer.
THe Dept of Energy requires a minimum efficiency of 99.01% per attached table.
Dept of Energy issued these required efficiencies on 10/12/07 for dry type transformers:
Single-Phase kVA
Efficiency
Three-Phase kVA
Efficiency
10
99.62
15
98.36
15
98.76
30
98.62
25
98.91
45
98.76
37.5
99.01
75
98.91
50
99.08
112.5
99.01
75
99.17
150
99.08
100
99.23
225
99.17
167
99.25
300
99.23
250
99.32
500
99.25
333
99.36
750
99.32
500
99.42
1000
99.36
667
99.46
1500
99.42
833
99.49
2000
99.46
2500
99.49