e57
Senior Member
- Location
- San Francisco, CA
2008 NEC - cycle in play in California...
How many outlets would be required on this Island?
Flat across entire top - has a sink and cook-top in it, and > 24" behind the sink and cook-top.
View attachment 8154
Per NEC just one.
But I am sure most people will install more than one.
>24" - however, the counter-top is not considered divided as there is far greater than 12" behind each. see 210.52(C)What is the dimensions from edge to range and edge to sink
It would be IF there were LESS than 12" behind either the sink or cook-top. This is much more than 12" - so it is ONE counter topIt is considered multiple counter tops so 210.52 (2) does not apply
It would be IF there were LESS than 12" behind either the sink or cook-top. This is much more than 12" - so it is ONE counter top
Since you have installed at least one receptacle according to 210.52(C)(2) and the space behind the sink and cook top is over 12", I would say you are compliant.