So recently I noticed an electrician switching on/off a 480V MCC main breaker for maintenance. The arc flash label on the breaker panel is marked 60 cal. I told him it's best to get a flash suit on for the following two reasons
1. Main breakers like this haven't been exercised for a long time, we don't know its condition
2. Arc flash cal. is high in this case, and the 480V panels are NON arc blast resistant, and I told him if there was a fault, it wouldn't make a difference if you had that panel in front of you or not.
His argument of not wearing the flash suit:
I only need the flash suit if I rack the breaker in/out, since there's no racking in/out action, I don't need the flash suit.
So, what's the correct action in this case? Any particular place on the NFPA 70E we can look to seek some clarifications?
Thanks.