DC voltage drop with length included..
mta145
Hoping that someone could help verify what i am getting...
Voltage is 420 DC
Load is 217 amps
Distance is 130'
Conductor is 300 mcm AL
I am coming up with 1% voltage drop is this correct?
420v DC
217 amps
Distance is 130'
Conductor is 3 sets of 2/0 AL
VD = .7%
Any help on this would be greatly appreciated
I get 2.4% for the first example and 2.7% for the second---but for some reason using the formula VD=2KLI/CM seems not exactly correct:?
K=12.9
L=130
I=217
CM= (First Ex) 300000 and 266200 for the second
300: At 167?F I get 0.95%
(3)2/0: At 167?F I get 0.712%
300: At 77?F I get 0.793%
(3)2/0: At 77?F I get 0.594%
K=12.9
L=130
I=217
K should be a direct current constant. Q would be an AC constant to be used when skin effect comes into play. Look at the difference in table 8 and table 9, in chapter 9 NEC.
AHA!!! I knew there was something tickling me that said I was incorrect!!!--Thanks Hv--That's what is so great about this forum, someone always has the answer and I (re)learn alot of stuff--especially as I am getting worse--that oldtimers disease, you know the one--CRS-- seems to be hitting more often (I know there is a reason but I can't remember where I read it):eek: or at least the wife says so!~
Thanks guys!!