OK, so here's the deal. I submitted calcs for review by the clients engineer and one of the comments that I got back said that my voltage drop calculation was wrong. Their engineer says that the voltage at a sub panel 200 feet from the MDP is the same as at the MDP? Did I fall asleep in class somewhere? Don't you always do a vd calc on a sub panel if for no other reason than to size the conductor and make sure you don't exceed the allowable drop?