725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors, and
Medium-Power Network-Powered Broadband Communications
Cables.
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compartment,
enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light,
power, Class 1, non–power-limited fire alarm circuits, and
medium-power network-powered broadband communications
circuits unless permitted by 725.136(B) through (I).
(B) Separated by Barriers. Class 2 and Class 3 circuits
shall be permitted to be installed together with the conductors
of electric light, power, Class 1, non–power-limited fire alarm
and medium power network-powered broadband communications
circuits where they are separated by a barrier.
(C) Raceways Within Enclosures. In enclosures, Class 2
and Class 3 circuits shall be permitted to be installed in a
raceway to separate them from Class 1, non–power-limited
fire alarm and medium-power network-powered broadband
communications circuits.
(D) Associated Systems Within Enclosures. Class 2 and
Class 3 circuit conductors in compartments, enclosures, device
boxes, outlet boxes, or similar fittings shall be permitted to be
installed with electric light, power, Class 1, non–powerlimited
fire alarm, and medium-power network-powered
broadband communications circuits where they are introduced
solely to connect the equipment connected to Class 2 and
Class 3 circuits, and where (1) or (2) applies:
(1) The electric light, power, Class 1, non–power-limited fire
alarm, and medium-power network-powered broadband
communications circuit conductors are routed to maintain
a minimum of 6 mm (0.25 in.) separation from the conductors
and cables of Class 2 and Class 3 circuits.
(2) The circuit conductors operate at 150 volts or less to
ground and also comply with one of the following:
a. The Class 2 and Class 3 circuits are installed using
Type CL3, CL3R, or CL3P or permitted substitute
cables, provided these Class 3 cable conductors extending
beyond the jacket are separated by a minimum
of 6 mm (0.25 in.) or by a nonconductive sleeve or
nonconductive barrier from all other conductors.
b. The Class 2 and Class 3 circuit conductors are installed
as a Class 1 circuit in accordance with 725.41.